Hospital clean room HVAC causing crazy demand spikes

Started by Donna H. — 14 years ago — 38 views
Got a regional hospital with a new surgical suite that includes several clean rooms. Their demand charges have tripled since the renovation - hitting $47K last month alone. The HVAC systems for these rooms run 24/7 and apparently have some kind of pressure monitoring that kicks in additional equipment randomly. Anyone dealt with medical clean room energy issues?
Donna - clean rooms are energy hogs by design. The pressure cascade systems often cycle on/off based on door openings and air quality sensors. You might want to look at demand response options or battery storage to shave those peaks. Some hospitals have saved 30-40% on demand charges with proper load management.
Had a similar issue with a cardiac cath lab expansion. Turned out the HVAC contractor hadn't programmed the staging properly - everything was coming online at once instead of sequenced starts. Fixed the controls and demand dropped by 200 kW. Might be worth having an energy engineer review the system operation.
Steve that's a great point about the staging. I'll suggest they bring in an HVAC controls specialist. These demand charges are killing their budget and they're threatening to just shut down the clean rooms during peak hours, which obviously isn't an option.
Just a heads-up for newer auditors: if your engagement letter doesn't clearly say what happens when the utility issues a credit on a future bill (vs. a check refund), you can end up arguing with the client about whether you've earned your fee. Mine now defines 'recovered' as 'any monetary benefit including bill credits, check refunds, or written rate adjustments effective on a future bill cycle.' Client lawyers tend to be fine with that wording.