Stan A. from Boise. Idaho Power just energized our new warehouse service last month. 480V 3-phase, estimated load around 150kW peak. They installed 400:1 CTs and set the multiplier accordingly, but our actual usage is running about 80-90kW and the bills seem way too high for a Schedule 19 account. I think they over-spec'd the CTs. The load calculations showed we needed maybe 200:1 CTs max. Anyone dealt with utilities installing wrong CT ratios on new services? Do we have any recourse or are we stuck with the 400:1 setup?
Member Community
Enter your email to read this discussion
You're reading the AAUBA Member Forum — where Certified Utility Bill Auditors share case studies, tariff strategies, and industry insights.
Free to read. Enter your email to continue.
No spam. We'll send you one welcome email about CUBA certification. Unsubscribe any time.
New service install - wrong CTs from day one
Wendell T. from Billings. NorthWestern Energy did similar to us - way over-sized the CTs for our actual load. The problem is accuracy at low load factors. 400:1 CTs reading 80kW are only running at 20% of capacity, which reduces meter accuracy. You should be able to request different CTs if your load doesn't justify the 400:1 ratio. Utilities usually size CTs for 120-150% of expected peak load.
Randy Dawson here. Stan, this is more common than you'd think with new services. Utilities often over-size CTs as a safety margin, but it can hurt accuracy at lower loads. The key is your load study and actual usage data. If your peak load is consistently under 120kW, you have a legitimate case for 200:1 CTs instead of 400:1. Idaho Power should be willing to discuss this, especially if you can show 6-12 months of actual usage data. The CT change itself isn't expensive for them - it's mainly labor. Push back on this if your bills seem high relative to actual consumption.
Greg L. from Indianapolis. Had this fight with AES Indiana on a new manufacturing facility. They wanted 600:1 CTs for a 200kW estimated load. We pushed back with load calculations and they agreed to 300:1. The difference in billing accuracy was significant at our actual operating levels around 120-140kW. Don't let them over-engineer your metering setup.
Thanks for the advice. I've been tracking our actual peaks and we're hitting 95-105kW max, well under the 400:1 CT capacity. Idaho Power said they'll review but want 3 months of usage history first. The December bill was $4,200 which seems high for our actual consumption level on Schedule 19.
Janet K. from Cincinnati. Duke Energy has a formal process for CT ratio review on new services. You file a request with your account manager and they'll do a field assessment. The 3-month requirement is pretty standard - they want to see your actual load patterns before making changes.
Final update - Idaho Power agreed to change to 200:1 CTs after reviewing our December usage data. Peak load was only 98kW so the 400:1 setup was definitely oversized. They're scheduling the CT swap for early January and will adjust the December bill once the new multiplier is active. Sometimes persistence pays off.