ComEd demand threshold crossing - client jumped from 100kW to 850kW

Started by Susan P. — 10 years ago — 14 views
Interesting situation with a data center client in Chicago. They were happily on ComEd Rate BGSGS (Secondary General Service) with 80-100kW demand for two years. Added server capacity last month and hit 850kW peak. ComEd automatically moved them to Rate BGS (Primary General Service) but the demand charges are brutal - $16.83/kW vs previous $9.22/kW. Client is freaking out over $14K monthly bills. Any options for managing this transition? - Susan P.
Susan, once you cross ComEd's 400kW threshold you're automatically moved to primary voltage rates. The demand charge increase is painful but check if they qualify for Rate BGS-TOU (time of use). If they can shift some server loads to off-peak hours, the demand charge drops to $12.15/kW during off-peak periods. Also verify they're actually taking primary voltage service - if still on secondary they should be on Rate BGSGS-HT. - Randy D.
Randy's right about the voltage level. I had a similar ComEd account that was billed on primary rates but actually served at secondary voltage. ComEd corrected it and refunded 8 months of overcharges. Always verify the actual service voltage matches the rate schedule voltage requirements. - Sarah M.
Checked the service details - they're definitely on secondary voltage but demand over 400kW. ComEd rep says they automatically go to Rate BGSGS-HT (High Tension Secondary) at $14.52/kW demand charge. Still expensive but better than the $16.83 they're charging now. Filing a rate correction request. - Susan P.
Susan, also look at power factor penalties. Data centers often have poor power factor from all the switching power supplies. ComEd penalizes anything below 85% PF. Adding power factor correction capacitors might save more than you think. - Ed T.
Ed, good call on power factor. Last bill showed 78% PF with $2,100 penalty. Client is getting quotes for automatic PF correction equipment. Between the rate correction and PF improvement looking at $4K monthly savings. Thanks everyone. - Susan P.
This thread is gold for understanding ComEd's demand thresholds. I'm dealing with a manufacturing client who might cross 400kW next year. Better to plan for the rate change instead of getting surprised like Susan's client did. - Craig P.