REP contract has a hidden capacity charge — is this normal?

Started by Nancy P. — 5 years ago — 48 views
Reading my client's REP contract in Austin carefully. The headline rate is $0.058/kWh which is competitive. But buried in the terms is a "capacity obligation charge" of $4.50/kW applied to the client's peak demand. On a 400 kW account, that's an extra $1,800/month that isn't reflected in the per-kWh rate. The client had no idea this charge existed when they signed. Is this standard practice?
Not standard but not uncommon with certain REPs. The capacity charge covers the REP's cost of securing generation capacity from ERCOT. Some REPs bake this into the per-kWh rate, others break it out as a separate charge. The problem is when the REP quotes a low per-kWh rate to win the deal and then adds the capacity charge in the fine print. Your client isn't being overcharged per the contract — they're being charged exactly what the contract says. The issue is whether the REP disclosed this during the sales process.
Marcus is right — if the contract includes the capacity charge, it's technically valid. But this is worth flagging to the client as a lesson for their next contract renewal. When comparing REP offers, you have to look at the total cost including all charges, not just the headline per-kWh rate. For the audit, calculate the client's actual all-in cost per kWh (energy rate plus capacity charge divided by kWh) and compare that to what's available on the market. If the all-in cost is above market, the client should shop at their next contract renewal window.
All-in cost is $0.0725/kWh when I include the capacity charge. Market rates for this size account are around $0.062. So the client is overpaying by about $0.01/kWh. On 600,000 kWh/month that's $6,000/month they could save by switching at renewal. Flagging for the client. Thanks.