Demand charge on a client who is barely open — minimum billing problem

Started by Amir C. — 16 years ago — 29 views
Susan from Nashville. Client runs a seasonal flower shop — open full time February through May, limited hours June through January. The utility bills a minimum demand charge even during months when almost nothing is running. Last January the shop was barely open and the demand charge was $190 on a total bill of $220. Is there a path to reducing minimum demand billing for seasonal accounts?
Dave from Charlotte. The minimum demand charge is usually tied to the metered service size, not actual usage. Reducing it typically requires either downgrading the service to a smaller transformer and meter or switching to a seasonal rate schedule if one exists.
Susan again. The shop uses a large commercial refrigeration unit during the off-season even when nothing else is running. So the service can not be fully disconnected. But a smaller transformer might work.
Dave again. A service downgrade is a capital project — the utility would need to do the work and there is usually a cost. You need to model the payback period. If the minimum demand overcharge is $150 per month for 7 off-season months that is $1,050 per year. If the downgrade costs $2,500 the payback is about 2.5 years.
Frank from Portland. Also check whether there is a seasonal service option that allows a formal reduction in service level during off-season months at a lower minimum charge. Some utilities have this specifically for seasonal retailers.
Frank, what would I search for in the tariff?
Frank again. Try seasonal service, reduced service, and limited use. Also look at the rate schedule's definition of billing demand — some schedules have a lower minimum billing demand for accounts with documented seasonal operations.
Tom from Seattle. One more option — check if the refrigeration circuit could be served from a separate smaller service. Isolate the off-season base load onto its own meter and downgrade the main service during off months.